Gentlemen: Are there any installation requirements regarding the distance between the pressure gauge/thermometer at the outlet of the temperature and pressure reducer and the water spraying point?
Reply #22018-12-29
The installation locations of the pressure and temperature measurement points on the temperature and pressure reduction unit are usually provided in the drawings issued by the manufacturer of that unit. Generally, the layout of pressure measurement points on the drawings is fine; for temperature measurements to be accurate, the temperature points should usually be about 2 meters away from the outlet of the spray cooling device. Thermal resistor yunrun.com.cn/product/list_80.html
Reply #32018-12-29
Go as far away as possible; if the temperature is too close, it will be displayed as low. I’ve never paid attention to pressure!
Reply #42018-12-29
Under normal circumstances, the temperature and pressure measurement points of the temperature reducer are located on the outlet pipe of the device, near it – not too close nor too far – to ensure accurate measurements and sensitive control.
Reply #52019-01-02
The lower the temperature, the better; pressure doesn’t matter, as our steam pipeline network is very long, and what’s important is that the temperature at the end of the pipelines meets the required standards
Reply #62019-01-02
If conditions permit, an 8-10 times larger diameter would be better, right?
Reply #72019-04-17
Install local and remote temperature and pressure transmitters 2–3 meters away from the outlet of the temperature reduction regulator, in sequence
Reply #82019-04-17
Generally, manufacturers of temperature and pressure reducing devices provide a diagram; according to clause 10.1.1 of the NB-T47033-2013 standard for such devices, the temperature and pressure measurement points at the device’s outlet should be located more than 1 meter away from the outlet itself

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.