2019-04-17View Original

Thread Content

For the 24VDC power supply terminals, is it better to use circuit breakers or fuse terminals? Are there any relevant standard requirements?
Reply #22019-04-17
From the air switch to the switch box or fuse terminal, and from the switch box or fuse terminal to the instrument. If you’re wealthy and have enough space, it’s also fine to use a backup power source along with a circuit breaker.
Reply #32019-04-17
In fact, circuit breakers are only suitable for 24V main power supplies, as typical circuit breakers have a minimum rating of 6A, while instruments generally don’t require such a high current; fuses, on the other hand, can handle 1A. So unless it’s a higher current, it’s better to be safe
Reply #42019-04-18
Take a look at this specification. HG_T20509-2014 Specifications for Instrument Power Supply Design

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.