2019-07-12View Original

Thread Content

Four tips for zeroing the Rosemount 3051 transmitter: First, the simplest way to zero a Rosemount transmitter is as follows: there is a quick button on the gauge; one of these buttons corresponds to the S range, while the other corresponds to the Z zero point. You can press the Z button for a few seconds, and it will quickly set the current pressure to zero (outputting 4 mA). Second, use the Rosemount 475 handheld transmitter to zero it (that is, set the current pressure to zero). II. To change the range, use the Rosemount handheld controller (basic model: 475HP1ENA9GMT) to make the adjustment; additionally, press the quick button S to output the currently measured pressure as 20mA. III. The inaccurate readings on Rosemount gauges are mainly due to a discrepancy between the pressure displayed on the control unit and that shown on the gauge itself: 1. You can set the gauge’s range to match that of the control unit, and then reset it using the 475 communicator (however, this should be done occasionally only, as it can affect the gauge’s linear accuracy). 2. Achieve consistency with the main controller by changing the range of the table, and the method for this is to shift the range as a whole. IV. Calibration of Rosemount differential pressure transmitters: First, set the damping to zero. Adjust the zero point first, then apply the full-scale pressure to set the range so that the output is 20mA. After the zero point and full-scale settings are correct, check the intermediate scales to see if they are within the specified limits; make fine adjustments if necessary. Then, adjustments for migration, linearity, and damping are carried out.
Reply #22019-12-25
It turns out that the 3051CD and 3051TG series have external zero-setting buttons. Below the nameplate on the top of the transmitter. For the 3051DP and 3051GP series, external zeroing is an optional code.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.