Flow meter issues

2019-07-16View Original

Thread Content

After the manual valve was opened, the process flow rate was approximately 3 cubic meters; the opening degree of the associated control valve was 60, and the flow meter also indicated a flow rate of around 3 cubic meters. However, after some time, the valve remained at 60% open, and the manual valve didn’t move either. Yet the reading on the flow meter kept decreasing. The flow meter in question is a Yokogawa electromagnetic flow meter, and the fluid being measured is pure water. What could be causing this situation?
Reply #22019-07-16
If it doesn’t conduct electricity, an electromagnetic flowmeter definitely cannot be used; other types can be chosen, such as vortex flowmeters, turbine flowmeters, ultrasonic flowmeters, or positive displacement flowmeters – electromagnetic flowmeters are not an option in this case
Reply #32019-07-16
Do you mean desalinated water by pure water? If so, electromagnetism won’t work
Reply #42019-07-18
You definitely won’t get accurate measurements using electromagnetism
Reply #52019-07-18
Pure water uses electromagnetism. . . Pull out the one that was selected and kill it; it’s useless anyway if kept
Reply #62019-07-18
Is it confirmed to be pure water? Check the conductivity! There are also flow meter models
Reply #72019-07-18
Yokogawa does indeed have electromagnetic flowmeters for measuring low conductivity
Reply #82019-07-19
Who said that pure water cannot be measured using an electromagnetic flowmeter? All you need to do is add chemicals to the pure water. A good electromagnetic flowmeter can perform measurements when the conductivity reaches 20 μS/cm; domestic models may require a conductivity of 50 μS/cm.
Reply #92019-07-21
The medium measured by an electromagnetic flowmeter must be conductive. Is the pure water in your home conductive?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.