I ran into a problem today with Siemens’ SU200AI module: one of its channels is connected to a flow meter. The computer shows large fluctuations in flow rate, but the flow meter itself is stable, and the current readings are also stable. When checking the program on the computer, fluctuations are indeed present; the filtering settings are all correct. The fluctuations decrease when a signal generator is used to supply a signal, and I’ve also checked the grounding connections, ensuring that the M terminal is properly grounded. Yet, the issue of fluctuating readings persists. In the end, I even replaced the module, but the problem remained. Has anyone encountered this situation? Could you please offer some guidance? Please
Reply #22020-07-24
Ground the flow meter, use shielded twisted pair cable, add an isolation barrier, and so on
Reply #32020-07-24
Is the signal generated from the field primary meter? Is there a safety barrier?
Reply #42020-07-24
It is caused by line interference. A few people upstairs introduced the methods.
Reply #52020-07-24
Is the instrument cable unshielded, requiring single-ended grounding?
Reply #62020-07-24
It was tested through the direct connection as well as on-site, and the fluctuations are the same in both cases. All that’s left now is to replace the power supply cable; I’ll shut down the system and try connecting a new instrument power supply
Reply #72020-07-25
If there is an inverter in the distribution cabinet, add filtering
Reply #82020-07-25
Whether the power cable is shielded, or there is interference from high-frequency or low-frequency equipment on site, or from the power supply of other devices. I personally think it’s still a problem with the transmission channel.
Reply #92020-07-25
We have encountered this before: with 4 analog input channels, if they are not in use, they must be short-circuited; they cannot remain unused

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.