2022-10-30View Original

Thread Content

Dear experts, I would like to ask about the wiring conduit that runs downward from above: to what extent should its lowest point be below the wiring inlet of the instrument it is connected to? What are the relevant standards? Thank you
Reply #22022-10-31
It appears in 7.3.6 of SHT3019 and 8.4.7 of SHT3521; HGT20512 and GB50493 also have it, so I won’t check each one individually. The main purpose is to prevent rainwater from entering the instrument through the cables (being explosion-proof does not mean it is waterproof)
Reply #32022-10-31
Wrong, it’s GB50093 (GBT50493 applies to gases)

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.