I need help. As shown in the diagram below, a section should be set aside on the right side of the cable tray; the power cables for the motor should be placed in the larger area on the left side (the motor has a rated voltage of 380V, power of 110kW, and a current rating of 200A). The cables for the instruments should be placed in the smaller area on the right side (these cables are used for temperature probes and vibration sensors). I’m not sure if this approach is feasible. Is it okay if it’s not an analog signal? Are there any relevant standards? First, thank you all.
Reply #22019-12-10
Temperature and vibration are prone to interference; your power cable carries a high current, so it’s not suitable.
Reply #32019-12-10
Refer to standard HG/T20512-2014, P294
Reply #42019-12-10
It’s best not to do this, otherwise it will cause a lot of trouble later on.
Reply #52019-12-10
No, high-voltage and low-voltage circuits must be separated, as well as power supply and signals. Go and check the specifications yourself.
Reply #62019-12-11
No, high-voltage and low-voltage circuits must be separated, as well as intrinsically safe and non-intrinsically safe circuits
Reply #72019-12-11
There should be enough distance between the two to prevent interference

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.