Zone 2 explosion hazard, issue with instrument wire diameter

2019-12-20View Original

Thread Content

According to GB50058, Table 5.4.1-2 specifies that a wire thickness of at least 1.5 is required for Zone 2. However, per HG 20512, a thickness of 1.0–1.5 is acceptable for Zone 2. It is not clear whether 1.0 can be used for analog signals and digital signals in instrument control circuits; the distance is 350 meters. I seek expert advice on this matter. Thank you
Reply #22019-12-20
Anyway, the resistance is 6-7 ohms; I don’t know anything about the other values. The longest length I’ve used is 100 meters
Reply #32019-12-21
Theoretically, 1.0 is sufficient for 350 meters, but in practice it’s better to use 1.5 – there’s no need to save that little money.
Reply #42019-12-21
What I mean is that GB specifies a minimum of 1.5 for voltages below 1000V, while the specification for HG signal lines is different
Reply #52019-12-21
What is the relationship between explosion protection and wire diameter?
Reply #62019-12-21
There are requirements regarding the wire diameter in explosive hazard areas; take a look at the pictures I sent
Reply #72019-12-21
I want to ask what the relationship is between explosion protection and wire diameter.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.