Can another safety barrier be connected after a 1-in-2-out safety barrier?

2020-03-30View Original

Thread Content

The analog input safety gate MTL5544D used in SIS is of one-input two-output type, with output signals in the 4-20mA range. So, from this card to the DCS, is a safety barrier still required on the DCS side? Are there any regulations regarding this?
Reply #22020-03-30
There’s no need to connect anything further; it’s sufficient as long as the output wires of your 1-to-2 safety barrier are in the safe area. If they’re not in that area, then having a safety barrier in addition to the DCS is useless, and other explosion-proof solutions need to be considered.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.