Common faults of electromagnetic flowmeters and their solutions

2020-04-06View Original

Thread Content

Common faults of electromagnetic flowmeters and their solutions 1. No display on the electromagnetic flowmeter’s gauge 1. Check whether the power supply is connected; 2. Check whether the power fuse is intact ; 3. Check whether the supply voltage meets the requirements. II. Electromagnetic flowmeter excitation alarm 1. Check whether the excitation connections E*1 and E*2 are open circuit ; 2. Check whether the total resistance of the sensor excitation coil is less than 150Ω ; 3. If both of the above items are normal, then the converter is faulty. III. Alarm for empty tube in electromagnetic flowmeter 1. Check whether the fluid being measured fills the sensor’s measuring tube ; 2. Short-circuit the converter’s signal input terminals SIG1, SIG2, and SIGGND using a wire. If the “empty tube” warning is removed at this point, it indicates that the converter is functioning properly; the low conductivity of the fluid being tested or an incorrect setting for the empty tube threshold may be the cause ; 3. Check whether the sensor electrodes are functioning properly ; 4. Set the flow rate to zero, and observe that the conductivity ratio should be less than 100% ; 5. When current is flowing, the resistance between terminals SIG1T and SIG2 to SIGGND should be less than 50 KΩ (the values are measured with water as the dielectric; it is advisable to use an analog multimeter for measurement, and charging and discharging phenomena can be observed during the measurement process) ; 6. The DC voltage between DSI and DS2, as measured with a multimeter, should be less than 1V; otherwise, it indicates that the sensor electrodes are contaminated and need to be cleaned. IV. Inaccurate flow measurement by electromagnetic flowmeters 1. Check whether the fluid being measured fills the sensor’s measuring tube ; 2. Check whether the signal cable connections are proper ; 3. Check whether the sensor coefficients and zero points are set according to the sensor label or the factory calibration sheet.
Reply #22020-04-07
OP, you should specify the exact model of the electromagnetic flowmeter – different manufacturers use slightly different models. I still haven’t figured out how to check whether the fluid level in the pipe is full; meanwhile, fluctuations in the current flow meter are also a common issue. I hope the original poster can improve this.
Reply #32020-04-19
If the grounding is not proper, it is also possible for the reading to be zero

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.