Diagnosis of Siemens positioner faults

2020-08-26View Original

Thread Content

There is an FC control valve, using a Siemens positioner; diesel entered the instrument inlet pipe, and the positioner as well as other accessories were also affected. After the diesel was initially cleaned and the power was turned on, the valve immediately went to its fully open position. However, the self-check process gets stuck at the first step; logically, since the valve can open, the locator should be able to send a signal. Why then can’t it even proceed to the first step? By the way, at this time the valve makes no movement while in self-check mode. I hope the experts can help determine where the fault lies in the device for the students. Thank you.
Reply #22020-10-27
The diaphragm cannot hold air, so initialization cannot take place

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.