Recently, there has been a problem: with the FO control valve equipped with an intelligent positioner, it remains fully open when both the air supply and the signal line are disconnected. This is normal behavior. But once the signal wire is connected (with a current of about 4 milliamps), the valve closes completely. Shouldn’t it shut off completely only when there is a 20 milliampere current signal? (I remember that mechanical positioners shut off completely at a 20 milliampere signal.) It’s a new valve; the smart locator has not changed the direction of the signal input.
Reply #22020-11-06
It’s a problem with the system; the system air shut-off valve in the central control unit has a range of 0 to 100%, which corresponds to 20 to 4 mA. Try using a signal generator to see if the same phenomenon occurs
Reply #32020-11-07
Don’t overthink it; just solve the problem. If it can’t be solved or the situation keeps improving and worsening, replace it as soon as possible
Reply #42020-11-07
Don’t overthink it; just solve the problem. If it can’t be solved or the situation keeps improving and worsening, replace it as soon as possible
Reply #52020-11-07
Smart positioners can have forward and reverse actions set. Study hard*.
Reply #62020-11-07
In this control loop, if the control parameter (such as T) increases, does the process require the valve to be opened more or closed?
Reply #72020-11-08
The current status of the locator is that 4 mA corresponds to valve position 0, while 20 mA corresponds to valve position 100; the forward and reverse action of the locator can be adjusted accordingly
Reply #82020-11-09
This is probably due to an inversion on the control side; have them make the change there
Reply #92021-02-26
Issues with the settings of the intelligent locator: changing the direction of signal input
Reply #102021-02-26
What else can one do? That’s a question even vocational school students wouldn’t ask.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.