There is a standard orifice plate at the site used to measure the steam flow rate at 0.5 Mpa, and it often experiences large fluctuations as well as inaccurate measurements (usually on the low side). I would appreciate it if experts could check whether there is an issue with its installation
Reply #22021-02-20
1. The pressure guide tube is too short; there’s no point in installing a condensation tank. 2. The condensation tank is located higher than the pressure sampling point, causing the condensate to flow back
Reply #32021-02-20
The pressure tapping ports should be installed horizontally; the condensation tank should be made smaller. Insulation should be used to cover the three-valve assembly and components below it, but the gauge heads should not be covered as well.
Reply #42021-02-20
For measuring gases, it should be installed in this way: for measuring steam flow, the pressure tapping point must be located below, and there must be condensate present.
Reply #52021-02-21
Is the intention to shorten the pressure tap pipe to prevent surface freezing, or are there constraints regarding the installation location? The fluctuations are likely due to bubbles in the pressure guiding tube or in the condensation tank; if the flow rate is low, check whether there is internal leakage in the balance valve and whether the zero point has shifted. All aspects related to the DCS configuration must also be verified.
Reply #62021-02-22
Apart from installation issues, accuracy also requires voltage regulation compensation.
Reply #72021-02-22
It’s fine to install the steam unit facing upward, right? ? ? Discharge waste, check the zero point, remove and inspect for fouling on the orifice plate: lol
Reply #82021-02-22
It’s fine to install the steam unit facing upward, right? ? ? Discharge waste, check the zero point, remove and inspect for fouling on the orifice plate: lol
Reply #92021-02-22
The space is limited, so it’s not possible to install it horizontally; for maintenance reasons, it can only be installed at an angle upward
Reply #102021-02-22
Isn’t it true that a condenser tank is added because the pressure guiding pipe is too short? Its location is difficult to change, and steam heating will be required after making the changes

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.