HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Selection of pressure gauge range

2021-03-03View Original

Thread Content

Regarding the selection of the range for a pressure gauge, the question bank for instrument technicians suggests using elastic pressure gauges, with the maximum pressure not exceeding 3/4 of the gauge’s range. When the pressure being measured fluctuates significantly, the maximum pressure should not exceed 2/3 of the full range. To ensure accuracy, the minimum value of the pressure being measured should not be lower than 1/3 of the full range. Some sources state that the maximum pressure should not exceed 2/3 of the range, and in cases of large fluctuations in the measured pressure, it should not exceed 1/2 of the full range; again, to ensure accuracy, the minimum value should be at least 1/3 of the full range. Which of these two statements should be followed? Are there any standards regarding this?
Reply #22021-03-03
Specifications for the Selection and Design of Automated Instruments (HG/T 20507-2014) 5.2.8 The selection of the measurement range for pressure measuring instruments shall meet the following requirements: 1. When measuring a stable pressure, the normal operating pressure value should fall within the range of 1/3 to 2/3 of the instrument’s range. 2. When measuring the pressure of a pulsating medium (such as the pressure at the outlet of pumps, compressors, and fans), the normal operating pressure should be within the range of 1/3 to 1/2 of the instrument’s measurement range.
Reply #32021-03-04
\"Code for Selection and Design of Automation Instruments in Petrochemical Industries\" SH/T 3005-2016: 6.1.3 When measuring stable pressure, the normal operating pressure should be between 1/3 and 2/3 of the range. 6.1.4 When measuring pulsating pressure, the normal operating pressure should be between 1/3 and 1/2 of the range.
Reply #42021-03-04
Specifications for the Selection and Design of Automated Instruments (HG/T 20507-2014) 5.2.8 The selection of the measurement range for pressure measuring instruments shall meet the following requirements: 1. When measuring a stable pressure, the normal operating pressure value should fall within the range of 1/3 to 2/3 of the instrument’s range. 2. When measuring the pressure of a pulsating medium (such as the pressure at the outlet of pumps, compressors, and fans), the normal operating pressure should fall within the range of 1/3 to 1/2 of the instrument’s measurement range
Reply #52021-03-07
Is there something wrong with what’s stated in that instrumentation technician test booklet? Is the normal operating pressure 1/3 to 2/3, with a maximum of no more than 3/4? Is there such a specification?
Reply #62021-03-08
Regarding the maximum pressure of the pressure gauge, there are no regulations specified in the standard codes; each organization can set it according to its own circumstances.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.