This post was last edited by The one on 2026-7-10 09:44. \"Code for Blast Resistance Design of Petrochemical Buildings\" GB ∕T50779-2022 5.2.1 When the peak overpressure of the explosion shock wave is greater than 1.0 kPa and not more than 6.9 kPa, the exterior doors and windows used in blast-resistant buildings shall comply with the following requirements: 1. The glass installed in the exterior doors and windows of buildings shall be tempered glass or laminated tempered glass; 2. The exterior doors located at the building’s safety exits shall open outward, and automatic door closers shall be installed. 5.2.2 The blast-resistant protection doors used in blast-resistant buildings shall comply with the following requirements: 1. The door frames and doors shall be made of steel, and their fire resistance integrity shall not be less than 1.00 hour. 2. The structure and performance of the blast-resistant doors in personnel passages shall comply with the following requirements: 1) The dimensions of the opening should not exceed 1800 mm (width) × 2400 mm (height); 2) The door leaves should open outward, and automatic door closers as well as blast-resistant observation windows shall be installed. The door seals must remain intact when closed, and the doors should be able to open and function properly after being subjected to explosive loads; 3) The overpressure caused by the explosion shock wave on the interior door before isolation should be 50% of that caused by the explosion shock wave on the exterior door; 4) Both the interior and exterior doors should have a interlock mechanism that prevents them from opening at the same time, and this interlock should be automatically disengaged in case of a fire; 5) The glass in the blast-resistant observation windows must not break under explosive loads, and it should remain transparent even when heated on the outside. 3. The structure and performance of the blast-resistant doors for equipment passages shall comply with the following requirements: 1) The dimensions of the opening shall meet the requirements for equipment entry and exit, and such dimensions should not exceed 2400 mm (width) × 3000 mm (height); 2) Under the effect of explosive loads, the door may undergo permanent deformation, but it must not collapse entirely or have any components fall off; 3) The door leaves shall open outward, and no glass windows shall be installed; 4) Blast-resistant door locks shall be provided.
This post was last edited by The one on 2026-7-10 09:07. “Design Code for Petrochemical Control Rooms” SH/T 3006-2024, 4.4.10: The installation of control room doors shall comply with the following requirements: 1. Control room doors must meet safety requirements as well as those related to the entry and exit of equipment; 2. The number of doors leading from the control room to the outside shall be determined based on the floor area of the control room and the requirements of building design; 3. It is advisable to install an access control system in the control room; 4. There should be no doors in the cabinet rooms, operation rooms, and engineer’s rooms within the control room that lead directly to the outside of the building. 5. Access paths must be available at all times for emergency rescue equipment, emergency devices, and emergency exits. 4.10.1 An automatic fire alarm system shall be installed in the control room, and it shall meet the requirements of the \"Design Code for Automatic Fire Alarm Systems\" GB50116;
This post was last edited by The one on 2026-7-10 09:07. According to the \"Design Code for Control Rooms\" HG/T20508-2014, 3.4.11 stipulates that the installation of doors in control rooms shall comply with the following requirements: 1. They must meet safety requirements as well as those related to the entry and exit of equipment; 2. The number of doors leading from the control room to the outside should be determined based on the size of the control room and the requirements of building design; 3. Doors in control rooms with blast-resistant structures should be equipped with a separate vestibule serving as a buffer zone; 4. There should be no doors in the cabinet areas within control rooms that lead directly to the outside of the building. 3.9.1 An automatic fire alarm system shall be installed in the control room, and it shall comply with the provisions of the current national standard \"Code for Design of Automatic Fire Alarm Systems\" GB50116.
The following SH/T 3006-2024 is provided for reference.