Installation of thermocouple compensation wires

2021-04-18View Original

Thread Content

I have a question for everyone. Where does the thermocouple compensation wire start, and where does it end? For example, field thermocouple ----> junction box ----> control room terminal blocks ----> safety barrier ----> input card. Should the compensation wires then be laid from the thermocouple’s terminal blocks to the junction box, and finally to the input terminals of the safety barrier? Thank you all
Reply #22021-04-19
Theoretically, as long as it is an mV signal line of a thermocouple, compensation is required for accuracy.
Reply #32021-04-19
The length of the compensation wire is, in theory, used to extend the cold end of the thermocouple to a location where the temperature is stable. If the temperature at the field terminal box remains stable, the compensation wire is connected from the thermocouple terminal to the field terminal box.
Reply #42021-04-19
Remember, it’s sufficient if a compensation wire is connected between the wiring point of the thermocouple element and the input terminal of the input card.
Reply #52021-04-20
Thermocouple to control room terminal block
Reply #62022-09-22
Does that mean that one of the three wires in a thermistor, or one of the two wires in a thermocouple, must be a compensation wire?
Reply #72022-09-22
How do you always teach your child? Does a thermal resistor require a compensation wire?
Reply #82022-09-23
I’m sorry. That was a bit much to say
Reply #92022-09-23
It’s okay; I too end up having disputes with people in the electrical and instrumentation field, which is why I browse forums – after all, there needs to be some rules for avoiding arguments in the future, right?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.