Dear experts, I have a question: if the compensation wire of the thermocouple becomes loose within the thermocouple terminal box, will the DCS temperature reading be too high or too low?
Reply #22021-04-23
The thermocouple signal is in mV units. If the wiring is only loose but not disconnected, there is basically no impact; however, if the looseness leads to a disconnection, it’s not a matter of the signal being too high or too low, but rather the signal cannot be transmitted stably, resulting in significant noise.
Reply #32021-04-24
If one wire becomes loose, the DCS display shows an out-of-range value instantly; if both wires are loose, the value is too low.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.