Is the DEVCTL module necessary when configuring the pump status?

2021-06-16View Original

Thread Content

I would like to ask the experts: when configuring a circuit for pump operation, is it possible to use only DICHANNEL instead of a DEVCTL module? Can a diagram showing the operating status of the pump be obtained? Thank you!
Reply #22021-06-19
The PKS software can work fine without the DEVCTL module, as it has been verified.
Reply #32021-06-28
The Honeywell system still recommends using the DEVCTL block; it offers more comprehensive features later on – pulse output, constant output, as well as the possibility to add non-system operations and various functions such as alarms generated by feedback from pumps on site. If DI channels are used alone, only the pump status can be displayed, leaving out many functions
Reply #42021-06-29
Thank you! :handshake

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.