HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Purge rotameter and rotameter

2021-06-25View Original

Thread Content

In a data table, there is a PID diagram for the flushing water of the liquid level gauge in the coal chemical gasification furnace; in this diagram, the flow rate of the flushing water for the dual-flange liquid level gauge is indicated as PG. In the instrument data table, this is referred to as FICA, and its name is purge rotameter – PG represents the rotameter itself, and both of these instruments are installed locally. I don’t know the difference between these two. Those who take leave, please give me some advice.
Reply #22021-06-25
The category name at the top of this table is not visible, but since the control valve indicated above also mentions the field setting, this term \"on-site\" refers merely to installation at the site, and it does not mean that there are no remote transmission signals
Reply #32021-06-25
There’s no difference; the purge version just indicates its purpose!
Reply #42021-06-25
It’s the same thing – they’re all local rotor flowmeters!
Reply #52021-06-25
Essentially, they are all rotameters, but they have different uses. 1. FG is an indication function and does not participate in flow control. 2. The basic function of a purge flow meter is indication, but it provides a needle valve for adjusting the flow rate. The downstream user of the owner is the device port of the level gauge. Blowing is done to prevent high temperatures or clogging, thereby avoiding failures of the level gauge. FICV: Indicates that the flow meter is equipped with a constant-flow valve; when the pressure on the process side increases, the constant-flow valve opens automatically to maintain the preset purging flow rate.
Reply #62021-06-27
The 5th floor post explains it in great detail; just by looking at the abbreviations on the instruments, one can figure it out. F flow refers to flow rate, while G means local display – the original poster made a mistake. PG is an on-site pressure gauge. I indicates, C controls and adjusts, A triggers an alarm
Reply #72021-06-28
FICA is a flow indication and regulation alarm; it should be equipped with a transmitter for remote signal transmission
Reply #82021-06-28
FICA flow display adjustment alarm
Reply #92021-06-30
With different functions, FG is a flow meter for on-site indication, showing the instantaneous flow rate of the flushing water (main pipe); FICV is used to display and control the flushing water volume for each transmitter.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.