(Dry contact) When the DI channel is open, voltage is detected between the two terminals; when it is closed, no voltage is detected. What is the principle behind this?

2022-08-06View Original

Thread Content

(Dry contact) When the DI channel is open, voltage is detected between the two terminals; when it is closed, no voltage is detected. What is the principle behind this?
Reply #22024-01-28
This post was last edited by hanhaigang128 on 2024-1-28 at 11:19. When the DI switch contacts of a typical DCS or PLC are open, the voltage drop across those two contacts is 24VDC. When the normally open contacts close, the voltage across the two contacts is the same as 0VDC; therefore, the voltage drop between the two contacts is 0. In some PLCs, the DI inputs are 220VAC; similarly, when the normally open contacts close, the AC voltage across those two contacts with respect to ground is the same, so the voltage drop between the contacts after they close is 0.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.