There are currently two combustible gas detectors; the on-site readings show 0, the current measurement is 4 mA, while the readings on the host computer are 4.8 and 9.02. The card channels have also been replaced, but the readings remain unchanged. I would like to ask what’s going on here?
Reply #22023-02-17
Three-wire combustible gas alarm? If so, carefully check whether the signal lines and common terminals are connected correctly.
Reply #32023-02-18
You must have measured 4MA on-site; this only indicates that there is nothing wrong with the combustible gas alarm itself. You also need to check on the side of the card whether the incoming current is 4mA. It’s possible that the wires are connected incorrectly What if the safety barrier is broken? Check carefully and avoid taking things out of context.
Reply #42023-02-18
It works normally after replacing the third channel.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.