【2025 Benchmark Case】On-site Instrument Hazards Case (2/2)

2025-06-25View Original

Thread Content

1. Clause 5.7.1.2 Account Management of GB/T 33009.2-2016 \"Network Security for Industrial Automation and Control Systems – Distributed Control Systems (DCS), Part 2: Management Requirements\" This requirement includes, but is not limited to: a) A DCS account management process and policy should be established; account levels should be defined based on various security requirements, and the procedures for using DCS accounts should be standardized; The DCS account management processes and strategies are also reviewed regularly; if any shortcomings or defects are identified, these management processes need to be revised ; b) Accounts should be classified in accordance with the DCS security authorization policy, and corresponding access rights should be assigned; there should also be the capability for unified account management ; c) It shall be ensured that all authorizations, changes, and terminations of accounts are carried out through the appropriate authorization management process ; d) Record the access accounts for all DCS operation nodes, including the user, the device being accessed, permissions, and the administrator, etc ; e) Secure account management should be implemented for the process communication between DCS operation nodes such as operator stations and engineer stations, and control stations/controllers ;
Reply #22025-06-25
2. The grounding wire is wrapped around the grounding bolt. Article 6.3.3 of HG/T 20513-2014 \"Code for Grounding Design of Instrumentation Systems\": 6.3.3 All connections in the grounding system shall ensure good electrical conductivity. The connections between the grounding wires, grounding branch lines, grounding main lines, main grounding conductors, as well as grounding busbars and grounding collection plates should be made using copper terminals and galvanized steel bolts, along with anti-loosening and anti-slipping devices, to ensure a firm and reliable connection.
Reply #32025-06-25
3. Article 7.1.10 of the \"Code for Construction and Quality Acceptance of Automated Instrumentation Projects\" (GB 50093-2013): When cables enter panels, cabinets, or boxes, they should do so from the bottom, and waterproof sealing measures must be in place. Article 3.4.7 of the \"Specifications for Control Room Design\" HG/T 20508~2014: In operation rooms and engineer work areas, anti-static and anti-slip building materials that do not generate dust should be used ; Originally, it was an anti-static floor with an insulating pad added; static electricity couldn’t be conducted away. Insulating rubber was also used, just like in the power distribution cabinet.
Reply #42025-06-25
4. Article 6.3.1 of the \"Code for Grounding Design of Instrumentation Systems\" (HG/T 20513-2014): 6.3.1 All grounding connection wires shall be properly insulated before being connected to the grounding busbar; All grounding branch circuits must be properly insulated before connecting to the grounding junction box ; All grounding mains must be properly insulated before connecting to the main ground plate. 6.3.2 Ground busbars, ground collection plates, and main grounding plates shall be fixed using insulated brackets.
Reply #52025-06-25
5. Article 5.0.14 of the \"Code for Design of Safety Instrumentation in Petrochemical Industries\" (GB 50770-2013) stipulates that redundant technologies should be employed for components such as the central processing unit, input/output units, communication units, and power supply units of logic controllers.
Reply #62025-06-25
6. Article 4.2.9 of the \"Code for Construction and Acceptance of Grounding Systems in Electrical Installation Projects\" (GB 50169-2016) stipulates that the grounding of electrical installations must be connected separately to the grounding busbar or grounding grid; it is strictly prohibited to connect two or more electrical installations that require grounding in series through a single grounding wire.
Reply #72025-06-25
7. Article 10.3.6.12 of the \"Specifications for the Selection and Design of Automation Instruments in the Petrochemical Industry\" (SH/T 3005-2016): The manual and automatic positions of the handwheel must be clearly marked, and the automatic position shall be equipped with a locking mechanism.
Reply #82025-06-25
8. According to Article 4.2.1.4 of the \"Code for Construction and Acceptance of Electrical Installations in Explosive and Fire-Hazardous Environments\" (GB 50257-2014), the fastening bolts at the flameproof joints must be complete, and anti-loosening devices such as spring washers must be present in good condition.
Reply #92025-06-25
9. Article 7.4.8 of the \"Code for Construction and Quality Acceptance of Automatic Instrumentation Projects\" (GB 50093-2013): Flexible pipes should be used to connect cable conduits to sensing elements or field instruments, and waterproof bends should be provided. When connecting to field instrument boxes, junction boxes, wiring boxes, etc., it must be sealed and firmly fixed.
Reply #102025-06-25
10. It is not explosion-proof to insert two wires into one inlet hole of the explosion-proof wiring box for analytical instruments. According to Article 10.1.3 of the \"Code for Construction and Quality Acceptance of Automated Instrumentation Projects\" (GB 50093-2013), when introducing cables for explosion-proof instruments and electrical equipment, explosion-proof sealing rings or sealing fillers should be used for sealing; one hole in the elastic sealing ring should be used to seal one cable.
Reply #112025-06-25
11. Article 12.1.5 of the \"Code for Acceptance of Construction Quality of Petrochemical Instrumentation Projects\" (SH/T 3551-2013): Before the gas supply enters the instrumentation, a filtering and pressure-reducing device should be installed, and it should be mounted vertically.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.