This post was last edited by The one on 2026-6-9 16:04. I. Fault diagnosis during operation (without disassembly, quick on-site inspection) 1. Air leakage and abnormal noises (the most common symptom): Continuous hissing sound from the exhaust hole on the spring side of the actuator, air escaping from the gaps in the diaphragm head housing; the regulator keeps replenishing air frequently, resulting in a sharp increase in air consumption. Soap solution is applied to the head flange and exhaust port; continuous bubbling occurs → the diaphragm is punctured and air leaks, so it must be replaced.
2. Abnormal valve stroke: (1) Unable to open fully/cannot close completely: With a rated air supply pressure of 0.02~0.1 MPa, the valve position does not reach 0%/100%; increasing the air supply pressure does not improve the situation. If the valve core is not stuck and the packing is not too tight, then the issue lies in insufficient diaphragm thrust.
(2) Slow response, failure to move in response to small signal changes, and valve position drift: With the DCS setpoint remaining unchanged, the valve deviates from its intended position; the actuator attempts to correct this deviation repeatedly, and there is slight leakage from the diaphragm.
(3) No movement at all: After ventilation, the valve stem does not move at all; when the output air pipe is closed to maintain pressure, the pressure drops rapidly after air supply, resulting in a large tear in the diaphragm.
Simple airtightness test: Remove the air outlet hose of the locator, seal the end of the hose, supply air at 0.14 MPa pressure; if the pressure gauge shows rapid pressure drop, the diaphragm is damaged and the unit must be discarded.
II. Assessment of the disassembled appearance: Perform a visual inspection by opening the film removal head; replace it immediately if any of the following conditions are observed. 1. Cracking and damage: Holes, cracks, and fine surface fissures (caused by rubber aging) are present at the central push rod and along the outer sealing edge.
2. Elastic failure: When pressed, the diaphragm becomes hard and does not rebound, or it becomes soft and sticky, as well as swollen and bulging; The normal gel membrane returns to its original state quickly when pressed.
3. Corrosive degradation: The medium penetrates into the diaphragm head, causing the diaphragm to change color, develop layers and bubbles, and become swollen or deformed due to oil and gas or acids and alkalis.
4. Permanent deformation: Wrinkling and warping occur at the edges, preventing it from fitting flat against the membrane chamber.
IV. Forced replacement under special operating conditions: 1. Water in the air supply causes freezing, leading to frequent overpressure shocks on the actuator. 2. Process medium penetrates into the actuator and erodes the diaphragm. 3. Repeated tightening of the bolts during maintenance still failed to eliminate air leakage from the diaphragm head.
Distinguish: Packing/valve core failure ≠ damaged diaphragm. The valve resumes its normal operation after loosening the packing gland on the valve stem → the packing is too tight; If the valve spool gets stuck, the valve body must be disassembled; if the problem persists after that, it is then a membrane issue.