Failure of pneumatic diaphragm control valve

2009-12-31View Original

Thread Content

Our company has pneumatic diaphragm control valves (air-actuated valves) that need to be set at 80% in order to close, and at 30% in order to open. What could be the reason for this?
Reply #22010-01-01
““The pneumatic diaphragm control valve (air-actuated valve) needs to be set at 80% in order to close, and it must be set at 30% in order to open.” I’m not sure if this is expressed correctly The possible reason is that the mechanism of action is reversed and not properly adjusted.
Reply #32010-01-01
Possible reasons: 1. Zero point, the stroke is not properly adjusted. 2. The positioner is faulty or the feedback cam in the positioner is used incorrectly. 3. Low air supply pressure.
Reply #42010-01-01
Re-calibrate zero point and travel distance; Try replacing it with a valve positioner from a regulator of the same type.
Reply #52010-01-01
The original poster didn’t explain it clearly; does it mean that the system should be turned off when the input signal reaches 80% (i.e., 16.8 MA), and turned on when it reaches 20% (7.2 MA)? If that’s the case, then as mentioned above, the way it works must be reversed.
Reply #62010-01-01
It seems like your itinerary isn’t set up properly; recalibrating it should fix the issue
Reply #72010-01-01
Agree with the person above; is there something wrong with the description given by the OP? It’s so confusing!
Reply #82010-02-07
This situation cannot occur once it has been properly debugged. I’ll ask about it – what’s the stroke and linearity of the valve?
Reply #92010-02-08
It seems the original poster didn’t express themselves clearly! It seems that the mode of operation was selected incorrectly; recalibrating it should resolve the issue

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.