Regarding the failure of the EJA118W double-flange level gauge

2019-04-27View Original

Thread Content

Our plant has a double-flange level gauge installed. The temperature on the positive pressure side is around 180 degrees Celsius, while the temperature on the negative pressure side is 30 degrees Celsius. When it rains, the level indication keeps dropping, falling from 50% to 20% within two minutes. Today we conducted an experiment: we poured water on the positive pressure side, and the level dropped sharply; as the temperature increased, the level gradually returned to its original value. What could be the reason for this? Changing to a double-flange version gives the same result
Reply #22019-04-27
Are capillaries provided on both sides, or is it installed directly on the positive pressure side?
Reply #32019-04-27
If both sides are equipped with capillaries, it is recommended to consult the manufacturer. If it is unilateral, then the selection was incorrect from the start; generally, when the medium temperature exceeds 120°, it cannot be installed directly
Reply #42019-04-27
Consult the manufacturer; there is a dog leash available. What’s there to consult about? It’s just that the temperature coefficient is high, resulting in large temperature errors – errors as big as dog shit in a basin. :Bro P has said it many times: a double-flange gauge is just a low-precision, rough pressure measuring instrument. Use it as a makeshift solution; don’t complain. That’s about the best quality the manufacturer can offer – it’s just that good. Asking them for more is pointless; the performance isn’t that great. Try to keep the temperatures at both ends of the remote sensing capillary the same when using it. Try to use it at a constant temperature. . .
Reply #52019-04-28
This is due to silicone oil; at low temperatures, it is recommended to use two pressure transmitters to measure the differential pressure, rather than using a capillary
Reply #62019-04-28
On the same floor, the temperatures are different; using double flanges isn’t reliable… It’s caused by the thermal expansion of silicone oil! ! !
Reply #72019-04-28
What is the pressure inside the container? Is there a negative pressure condition? Judging from the symptoms, it seems to be a problem with the liquid filling the capillaries on both sides. Under normal conditions, this temperature is not considered high, and ordinary silicone oil should be fine; it is suspected that the filling liquid has started to vaporize.
Reply #82019-04-28
Yes, directly installed on the capillaries on both sides
Reply #92019-04-28
The pressure is not high, around 20 Kpa; there is no negative pressure

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.