Siemens M430 always stops due to F001 error alarm

2018-08-18View Original

Thread Content

After one of the inverter units in the company was damaged, a new one was installed with the same parameters as before. The motor and cables were checked and found to be in good condition. Now, after the motor runs for a while, it triggers an F001 error alarm and stops operating. It’s happened many times over, and I don’t know why. I would appreciate it if experts could offer some guidance and answers.
Reply #22018-08-20
The F001 error code on the Siemens M430 inverter indicates an overcurrent condition, which suggests a short circuit or grounding fault either in the motor’s cables or within the motor itself. Based on the symptoms you described, it is unlikely that there is a short circuit or grounding fault; rather, it is likely that the parameters of the inverter are set incorrectly, such as the motor’s rated current, rated voltage, rated frequency, and the inverter’s own rated parameters. The possibility of incorrect parameter settings is quite high; Additionally, the equipment is indeed experiencing overcurrent, so it is correct for the inverter to trip due to overcurrent.
Reply #32018-08-31
We’ve already burned one before; have we checked the cables on site and confirmed whether there are any issues with the motor? Also, are the parameter settings correct? Is the control mode voltage-frequency ratio or vector control? Is the motor operating under light load or heavy load? Motor current, power, right? Are there any issues with the on-site operation? Is there any long-term low-frequency operation? These are all things you should verify on-site: lol
Reply #42018-10-17
Is the inverter input powered continuously, or only during startup?
Reply #52018-10-18
For inverter overcurrent protection, with the field wiring and basic parameters remaining unchanged, it is necessary to check the load type as well as the V/F curve settings of the inverter in order to extend the startup time; P; P; P

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.