2022-05-11View Original

Thread Content

Article 5.5.1 of GB50650: “Metal tanks shall be provided with grounding for protection against direct lightning strikes. There shall be no less than 2 grounding points, which shall be evenly distributed around the perimeter of the tank. The distance between the grounding wires shall not exceed 18 meters.” ”Why isn’t it stated here that the distance between grounding points should not exceed 18 meters?
Reply #22022-05-12
The grounding of metal tanks is generally symmetrical and even; there is no specific spacing required, as it mainly depends on the diameter of the metal tank.
Reply #32022-05-12
If the tank does not meet the requirements for use as a down conductor, a separate down conductor must be installed; of course, the spacing between down conductors is not the same as the spacing between grounding points
Reply #42022-05-19
There are prerequisites for using a tank as a lightning receptor; first, it is necessary to determine whether it is suitable or not
Reply #52022-05-21
Going any further would deviate from the topic; I just want to know why only the spacing between the down conductors is specified, while the spacing between the grounding points is not
Reply #62022-05-23
Which way is it off? The down conductor and the grounding point are two separate things; can a distance of 18 meters between the grounding points be considered equivalent to the distance between the down conductors?
Reply #72022-05-27
Are there any requirements regarding the spacing between grounding points?
Reply #82022-06-02
The down conductor and the grounding point are two different concepts.
Reply #92022-06-10
Then, is there any requirement regarding the spacing between grounding points? Is it also 18 meters?
Reply #102022-06-13
Hello: Article 5.5.1 of GB50650 states that “metal tanks shall be provided with grounding for protection against direct lightning strikes; there should be no fewer than 2 grounding points, which shall be arranged evenly around the perimeter of the tank, with the distance between these grounding wires not exceeding 18 meters.” This clause already specifies that the grounding points should be arranged evenly along the tank body. There is another guideline that can be referred to: According to Article 14.2.1 of the GB50074-2014 Code for Design of Oil Depots, the distance between grounding points should not exceed 30 meters. So it can be understood as: the spacing between down conductors should not exceed 18 meters. The grounding points should be evenly distributed along the tank body; there must be no fewer than two such points, with a distance between them not exceeding 30 meters.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.