During the major maintenance of the unit, a high furnace pressure interlock was installed at -5 kPa. However, the pressure in our furnace fluctuates greatly; it might become positive pressure as soon as the viewing window is opened!

2021-11-17View Original

Thread Content

Moreover, the interlock is connected to the constant-light device as well; as an operator, one still doesn’t feel confident, because it’s not possible to turn on so many burners in such a short time!
Reply #22021-11-17
I would like to ask whether it is possible to eliminate such instantaneous fluctuations in DCS, thereby reducing the likelihood of interlocks occurring
Reply #32021-11-19
It was written incorrectly as -5pa. Upon closer inspection, the interlock condition requires it to last for 10 seconds
Reply #42021-11-21
Increase the frequency conversion of the exhaust fan to keep the negative pressure in the furnace away from the interlock value

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.