2020-05-14View Original

Thread Content

Requirement 3.2.11 h of Q/SY 1431-2011 states that —— the grounding terminal dedicated for static electricity must be more than 1.5 m away from the oil loading and unloading ports. What are the reasons given? Please have the experts conduct an in-depth analysis; thank you~
Reply #22020-05-15
It is probably because safety distances during loading and unloading need to be considered, so too close is not advisable
Reply #32020-05-15
Q/SY1431-2011 3.2.11 h specifies that the distance between the connection point of the static grounding wire and the tank truck and the filling port should be greater than 1.5 meters; Currently, the static grounding of tank trucks is accomplished using static clamps ; The gripping point of the clip is the connection point ; Given that the clamps used by most manufacturers are not explosion-proof, and there is a risk of them loosening during the unloading process, resulting in unstable connections that could lead to sparks, this 1.5-meter distance is provided to ensure that the connection points remain in explosion-proof zones 0 and 1 ; You may consider the clamps with explosion-proof certificates offered by Shijiazhuang Beian Technology ;
Reply #42020-05-16
It’s probably to prevent oil and gas from splashing onto the terminals and causing a fire
Reply #52020-05-17
Prevent discharge from igniting the volatile vapors around the discharge port.
Reply #62020-05-17
Prevent discharge from igniting the volatile vapors around the discharge port.
Reply #72020-05-19
Oil and gas evaporate from the pipe outlet; the area within 1.5 meters is a zone prone to explosions, and static discharge during terminal connection can easily generate sparks
Reply #82020-05-21
Regarding the safety distance issue, consider that static electricity clamps may generate sparks

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.