2018-01-26View Original

Thread Content

This post was last edited by liaifeng on 2018-8-3 at 22:34. In the pre-deethanization process, during startup, the liquid level in the reflux tank rises suddenly and at a very fast pace; this rise needs to be controlled by opening the light hydrocarbon discharge valve of the reflux tank. Along with the increase in liquid level, the temperature at the 12th tray of the deethanization tower also rises. The tower pressure, reflux, tower pressure difference, and bottom temperature are all stable; no cause can be identified. I hope everyone can help analyze this issue. Thank you!
Reply #22018-01-26
Control the heat input to the tower bottom; ensure stable reflux, and check whether the reflux pump is not delivering sufficient flow
Reply #32018-01-26
The reflux pump is functioning properly, and the heat source at the bottom of the tower is also stable
Reply #42018-01-26
1. Is the temperature of the material too high due to a short parallel operation time when your gas/liquid phase dryer is put into use? Second, is there any fluctuation in the reboiling heating at the bottom of the tower, especially in the unit that uses wash water?
Reply #52018-01-28
What should be the liquid level control for the propylene refrigerant in the tower top heat exchanger?
Reply #62018-03-01
It’s a bit like having overflow; reduce the steam slightly so that less material evaporates
Reply #72018-03-01
You were right; after the issue was resolved, we analyzed and found that it was caused by improper handling of the flooding phenomenon, which led to the tower being flooded

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.