Is there a flow deviation in the return pipe at the top of the water cooling tower, causing no water to flow out from one of the pipes?

2018-06-05View Original

Thread Content

Circulating water is required in the process flow; two cooling towers have been installed. At the far end of the return pipe, there is a 90° elbow that leads directly to the water inlet on the side of the water cooling tower, and there is also a tee connecting to the water inlet on that same side of the water cooling tower. The current situation is that customers report an increase in the temperature of the circulating water. Upon inspection, it was found that there is water only at the outlet on the far end, while there is no water at the inlet at all – not a single drop. The return water pressure measured is 0.202 MPa. Only one main return valve is installed for the return water; the span of the pipes is 1.5 meters, and their vertical height is 3.9 meters. Return pipe DN150. May I ask why this is?
Reply #22018-06-05
The pump’s outlet pipe is 150, and the two branch pipes also have no valves and are 150 as well. One is a 90° elbow, and the other is a tee.
Reply #32018-06-05
Water will definitely flow in the direction where there is less resistance. You can install a valve at the far end to increase the pipeline losses there accordingly. Otherwise, change the distribution pattern of the tee, from inlet in the middle to outlets at both ends, so that the layout of the branch pipes is the same. You can also try using a Y-shaped tee.
Reply #42018-06-05
Why doesn’t the other one have any water at all? And there are two pumps on site, connected in parallel. When both pumps are turned on, there is still no water
Reply #52018-06-05
What are the flow rate and head on the pump’s nameplate? Is the total flow rate of the two pumps over 150 cubic meters?
Reply #62018-06-05
The flow rate per unit is 50 cubic meters per hour, with a head of 39 M.
Reply #72018-06-05
The pressure inside the cold water towers is different; it seems there are two towers from the photos. How many cooling fans are there?
Reply #82018-06-05
The flow rate for a DN150 pipe isn’t high; add a valve at the far end to regulate it, thereby increasing the pipeline losses there. To allow water to flow out at the proximal end
Reply #92018-06-06
The water pipes are directed toward two collection trays at the top; they are of an open type and operate without pressure. There are two water towers on site, one in use and one as a backup, but only one can be seen in the photos. Two water pipes are directed at the same tower, which consists of a single fan with water intake on both sides.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.