2018-06-10View Original

Thread Content

Figure 1 is the distillation tower, and Figure 2 is the reflux drum curve of the distillation tower! There is no pressure in the top of the distillation tower; there is some pressure from time to time. The reflux tank can be used to supply pressure with fuel gas, but the tower still doesn’t develop any pressure! The temperature of the feed to the distillation tower is stable! The diesel flash point is required to be above 63; to meet the standards, the dry point of gasoline must be greater than 250. The feed ratio remains unchanged, but adjustments have been tried nonetheless, resulting in fluctuations in the concentrations of the components! The pump of the fractional distillation cycle furnace at maximum capacity
Reply #22018-06-10
Are there significant fluctuations in the air-cooling temperature and bottom temperature?
Reply #32018-06-10
The image is a bit blurry; it’s not very clear. The pressure in the reflux tank is controlled via proportional control by PIC72101. When there is no pressure in the reflux tank, according to the proportional control principle, valve A (the nitrogen filling valve) should be open while valve B (the vent valve) should be fully open. However, from your diagram, it appears that valve A is closed at 0%, while valve B is open at 50%. Please verify this. If the output is reversed, it’s easy to explain why there is no pressure in the reflux tank, and it’s also easy to explain the tower flooding.
Reply #42018-06-10
The pressure difference between the top and bottom of the distillation tower is normal. Whether or not the tower is filled affects the temperature; it rises by a few degrees after air cooling, while the temperature drops in the case of a flooded tower
Reply #52018-06-10
It appears to be divided in the diagram, but in reality it’s all in manual mode; pressure replenishment and venting are handled separately. The reflux tank is used to replenish pressure, and there’s no top pressure either. However, previously when the reflux tank was used to replenish pressure, the tower’s pressure would increase as well, because the dry point of the gasoline was high at that time; but now there’s no reaction in terms of pressure
Reply #62018-06-10
Look at the pressure; this could be the reason
Reply #72018-06-10
First, lower the temperature at the furnace outlet and adjust the reflux properly
Reply #82018-06-10
The reflux tank can compensate for the pressure loss, but the tower top cannot; have you checked for internal leakage in the safety valve at the tower top?
Reply #92018-06-11
The safety valve at the top of the tower is leak-free, and there is no pressure indicated on the gauge at the site as well

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.