Will the accuracy be affected if a diaphragm pump is used in front of the vortex flow meter?

2017-06-22View Original

Thread Content

May I ask if using a diaphragm pump in front of a vortex flow meter will affect its accuracy?
Reply #22017-06-22
Should we swap the two positions, with the flow meter placed at the front?
Reply #32017-06-22
It's sufficient to ensure there is enough straight pipe section; it's better to place it at the front
Reply #42017-06-22
It's sufficient to ensure there is enough straight pipe section
Reply #52017-06-22
Thank you all. I’m worried that the diaphragm pump may produce pulses, which could affect the flow rate.
Reply #62017-06-23
Ensure a straight pipe section, with no vibration or bubbles.
Reply #72017-06-23
Just ensure there is enough straight pipe section; no problem.
Reply #82017-06-23
One thing: for all flowmeters, the better the flow stability, the higher the accuracy. Try to keep things stable; installing a rectifier and current stabilizer is not ruled out
Reply #92017-06-23
1. Stay as far away as possible, so that the pulse can be smaller. 2. Adding a pulse buffer would work very well.
Reply #102017-06-23
It does have an impact to some extent; one thing is to ensure that there are sufficient long straight sections of pipe, the vibration prevention measures for the pipes also need to be properly addressed, and then there’s the issue of signal interference.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.