The ABB TZID-C self-tuning function doesn’t work; no error message is displayed. What’s the reason?

2015-06-14View Original

Thread Content

I spent four hours working on the ABB positioner today. No error messages appeared during the self-tuning process. When the display reached 40, the valve stem moved upward very slowly; moreover, it returned to 40 before reaching 100, after which the valve stem started moving upward again. This repeated itself numerous times, and it wasn’t possible to complete the tuning even after 10 minutes. What could be the reason?
Reply #22015-06-15
“The display shows that when it reaches 40, the valve stem moves upward very slowly; moreover, it returns to 40 before reaching 100, after which the valve stem moves upward again. Is this a problem with the valve?
Reply #32015-07-13
Last night, a new locator was installed. Due to the operation of the unit, full calibration was not used; instead, travel calibration was applied. The parameters of the original locator were simply set on the new locator – it might be worth giving it a try. P1.0 LINEAR, P1.2 FULL→STROKE, P2.3 DIRECT, P2.4 SHUT-CLS 5.0, P3.2 CTCLOCK, P8.2 DIRECT. P7.0 KP=2.0, P7.1 KP=4.0, P7.2 TV=145, P7.3 TV=58.
Reply #42015-07-13
Do I need to fill in all these fields? Did you succeed?
Reply #52015-07-13
After the tuning is complete, save and exit, switch to remote control; operations in the control room proceed normally. In fact, there are various types of self-tuning methods available, and manual tuning can also be used, as long as the system’s operational requirements are met.
Reply #62015-07-13
How can I detect an clogged amplifier, and how do I deal with it?
Reply #72015-07-20
If the amplifier is clogged, clean the oil and water from the air supply first; after re-supplying air, tap on the locator to remove the blockage. If the clogging is severe, replace the locator.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.