I have seen high-temperature thermocouples with a range of 0-1800 that could display values properly, and the high-temperature thermocouples being used now have a range of 100-1600 and can also indicate values correctly. Why is the range not 0 but 100?
Reply #22015-06-15
The display instrument shows the temperature based on the type of thermocouple set and the measured millivolt value; it has little to do with the set range, except in cases of temperature changes.
Reply #32015-06-15
K-type thermocouple, with a transmitter in between.
Reply #42015-06-15
Is this one of those thermocouples? ? It’s best to check the relationship between temperature and millivolts; in some cases, there are no millivolts below 100 degrees
Reply #52015-06-15
Why does this happen? Why do some have a value of less than 100 while others don’t?
Reply #62015-06-15
“A K-type thermocouple with a transmitter in between means that the 4–20mA signal output by the transmitter corresponds to temperatures of 100–1600°C. The advantage of this setup is that it makes it easy to detect a broken thermocouple; when the thermocouple is broken, the input terminal of the transmitter reads 0mV, and the transmitter’s output will be less than 4mA, resulting in a reading below 100°C, which allows for an initial determination that the thermocouple is broken.
Reply #72015-06-15
For example, a Type B thermocouple has a thermoelectric potential of 0.033 millivolts at 100 degrees. It’s impossible to measure such a small value; what type of thermocouple do you have? ? ? Also, what components are used in the entire circuit: is it connected to a safety barrier, to a card, or through a 4-20MA transmitter? ?
Reply #82015-06-16
It depends on the type. If temperature compensation is applied, it operates according to the range; if it’s simply incorporated into a template, then the range of the thermocouple doesn’t matter much

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.