Is a pressure interlock for the main burner of the heating furnace necessary?

2015-06-15View Original

Thread Content

The furnace was shut down due to the pressure interlock behind the constant-flame valve; is it necessary to have a pressure interlock behind the main burner valve as well?
Reply #22015-06-15
It is necessary to note that the pressure behind the constant-light valve does not represent the pressure at the main burner. Each is their own.
Reply #32015-06-15
So what if there is a pressure interlock on the main pipe? Can the pressure interlock behind the main burner valve be removed?
Reply #42015-06-16
The installation location of the fuel gas pressure transmitter involved in interlocking must be in front of the burner and behind the flame arrester, that is, between the flame arrester and the burner; any other location cannot represent the pressure before the burner.
Reply #52015-06-16
Is the fuel gas level often fluctuating? It seems you are also a colleague facing the problem of interlocks not functioning properly. Here’s a suggestion: if the processing speed of the control system is fast enough, check the difference between the measurement value before and after the transmitter; if this difference is too large, trigger an alarm but do not activate the interlock. What’s an appropriate difference.......... It tests the management of your organization! Hehe

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.