Can an electromagnetic flowmeter show an out-of-range value?

2016-10-26View Original

Thread Content

I would like to consult an instrumentation expert. There is an electromagnetic flowmeter installed on the pipeline, with a measurement range of 0–40. The rated flow rate of the pump is 40 m3/h, yet while the pump is operating, the flowmeter shows a flow rate of 47.8 m3/h. Can the electromagnetic flowmeter display a value of 47.8 m3/h when it is outside its specified range? Is this value of 47.8 reliable?
Reply #22016-10-26
This situation is similar to using a ruler with a 20 cm scale to measure the length of an A4 sheet of paper; if you end up seeing the 29.7 cm mark on the ruler, it’s clear that this is impossible. 】So it feels incomprehensible. 【So I suspect: what you see (0~40 is incorrect); the range of the electromagnetic flowmeter should be around 60. The control room has changed the program, and now the range is 0~60. Therefore, the value of 47.83 that you see is likely accurate.】 】
Reply #32016-10-26
The term ‘range’ has two meanings: the first is the range that the instrument itself can measure, and the second is the set range for the 4-20mA output of the instrument. The first is that inaccuracies occur when physical limits are exceeded; the second is that errors appear once manually set limits are surpassed. What you call the range resembles the second type, because the first type is generally not a whole number. So your display might be normal, and you need to change the settings of the instrument and the host computer.
Reply #42016-10-28
:Victory: The second floor is the correct answer; you can go to the settings of the electromagnetic flowmeter to check the 4–20mA range settings

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.