I would like to ask everyone: Instruments should be installed after the process pipelines have been purged. If the process pipelines have not been purged during construction and the instruments have already been installed, should those instruments be removed when purging is carried out? Does the instrument need to be pressurized separately? What should be done with various instruments during the pressure testing of process pipelines?
Reply #22015-06-19
Please help:lol:lol:lol
Reply #32015-06-19
It would be best to have relevant guidelines; I couldn’t find any
Reply #42015-06-19
Before purging and pressure testing, the instruments should be removed, and short stubs should be used in place of the flow meters and valve installations. Of course, those with a root valve can also have the root valve closed
Reply #52015-06-19
The sealing related to instruments involves pressure testing, leak testing, and airtightness testing, rather than pressure application
Reply #62015-06-19
I would like to ask everyone: Instruments should be installed after the process pipelines have been purged. If the process pipelines have not been purged during construction and the instruments have already been installed, should those instruments be removed when purging is carried out? Is it necessary to apply pressure separately in order to remove the instrument? It’s not necessary; the instruments are calibrated before being used and installed........ What should be done with various instruments during the pressure testing of process pipelines? It should be in a working state.
Reply #72015-06-19
During strength tests such as hydrostatic or pneumatic testing, it must be removed; After the strength test, for the leakiness test, everything must be reset before participating in the test.
Reply #82015-06-19
For those that need to be removed, the instrument doesn’t require separate pressurization!
Reply #92015-06-19
When blowing the whistle, we usually remove the instruments; for those that cannot be removed, blind flanges are installed at both ends to isolate them, and the blowing air is directed through alternative lines
Reply #102015-06-19
After disassembly, short-circuit it; the instrument can then be pressure-tested together with the process pipelines (such as during back-pressure testing)
Reply #112015-06-22
Thank you all for your help:lol

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.