Distance requirements between Class A storage tank areas and the corresponding transfer pumps

2015-06-19View Original

Thread Content

I would like to ask the experts here; I am currently working on a tank farm project. For Class A methane chloride storage areas, how far away must the transfer pump be from the tank wall? (What are the values for total volume >100 cubic meters or <100 cubic meters in meters?) Should it follow petrochemical regulations or building codes? The owner wants to make the storage tank as large as possible, but the space is limited! Thank you, let’s discuss it together
Reply #22015-06-19
It’s best to follow the strict rules. The standard that is stricter applies. Otherwise, it will be troublesome during the safety assessment and safety inspection.
Reply #32015-07-18
The transfer pump must be at least 15 m away from the tank wall, in accordance with clause 5.3.5 of the petrochemical regulations

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.