Vent pipeline of the liquid sulfur tank

2015-06-23View Original

Thread Content

Our company’s sulfur recovery facility produces 2,000 tons of sulfur per year; it features a three-dimensional design. The exhaust pipelines of the liquid sulfur tank are kept open for exhaust emission (the gas pumps are also running, with a low amount of steam being released). Is it normal for it to operate in this way? I saw on the forums that it is said the liquid sulfur tank operates under negative pressure. May I ask the experts: is the exhaust pipe also kept open to release gas during normal operation in your company?
Reply #22015-06-24
Increase the steam volume of the air extractor until no more steam is emitted.
Reply #32015-06-24
When starting up the extractor, it should be operated at a higher capacity and at a faster pace; once it is functioning properly, the steam supply can be gradually reduced to save on steam usage. Try it a few times and you’ll find an appropriate steam opening; generally, no adjustment is needed.
Reply #42015-06-24
Thank you! ! ! Just turn up the air extractor? Do the drain line valves need to be closed for normal operation?
Reply #52015-06-24
Oh, thank you! ! ! Do the drain line valves need to be closed for normal operation?
Reply #62015-06-25
Leave the drain line open; it allows you to determine the operating status of the air extractor. As long as the vent pipe doesn’t emit vapor, that’s fine.
Reply #72015-06-25
Why did you turn it off? Be careful not to deflate it;P
Reply #82015-06-25
My unit is indeed shut down; the exhaust pipeline is used only in emergency situations. It’s sufficient to adjust the steam valve of the extractor to an appropriate opening. If the exhaust pipeline remains open and the steam valve of the extractor is set to a too high opening, external air may enter, leading to spontaneous combustion of liquid sulfur.
Reply #92015-06-26
Oh, thank you! There are advantages and disadvantages to both turning it on and off.
Reply #102015-06-26
Thank you! If it’s not closed, air might leak into the liquid sulfur tank, right?
Reply #112015-06-26
Thank you! If it’s not closed, could air get into the liquid sulfur tank?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.