Regarding operating voltage

2015-10-08View Original

Thread Content

A temperature sensor at the site cannot be connected to the 375 handheld controller. The no-load voltage is 24V; once the temperature sensor is connected, the voltage drops to 17V. The paperless recorder is not receiving power. Is it a problem with the channels of the paperless recorder or an issue with the wiring? Thank you
Reply #22015-10-08
The temperature transmitter is new and there’s no problem. Thank you
Reply #32015-10-08
I’ve encountered many situations where the power for the instrument comes from a secondary meter, such as a flow meter; it’s quite common for the power to come from such devices. With this type of power supply setup, it’s often not possible for the 475 device to communicate properly with the instrument, but the problem is resolved as soon as another power source is used. I have solved the problem and found the cause: it was an electricity supply issue. However, I still don’t understand why the electricity output from the secondary meter causes this problem.
Reply #42015-10-08
I suggest you try replacing the power supply, using a signal generator or some other type of 24V mobile power source. Otherwise, check if there are any instruments nearby that can communicate properly, and borrow power from them to give it a try
Reply #52015-10-08
The power supply of the handheld controller at 24V is insufficient; it should be powered by a separate 24V power supply.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.