How to design SIS fail-safe interlocks?

2015-10-27View Original

Thread Content

Let’s take an example: for a valve closure via level interlock, the level switch is selected to be normally closed (it closes during interlock); then, based on the SIS logic output (0 or 1), the solenoid valve is activated for closure – but how should the relay be selected, as normally open or normally closed? For pressure interlock valve opening: the level switch should be selected as normally closed (to open during interlock), and then the SIS logic output (0 or 1) is used to interlock the solenoid valve (how should the relay be selected as normally open or normally closed?) When using two-way three-port solenoid valves, does it still matter whether to choose solenoid valves that are normally open or normally closed? It requires normal excitation, right? In general, I just want to know what a fail-safe interlock is On-site liquid level and pressure triggers are required (is it a normally closed switch?) ), must the SIS logic output also be 0 to achieve fail-safe operation? Also, for the relay that outputs the SIS logic, how should one choose between normally open and normally closed operation? Is choosing normally open the option that ensures fault safety? How to choose a solenoid valve? There is also the issue of normally open or normally closed operation. Please ask an expert to answer, thank you!
Reply #22015-10-27
SIS generally follows input 0 interlock, with the output also being 0 interlock.
Reply #32015-10-28
Safety interlock: It generally needs to be set to 0, and the output should also be 0. The solenoid valve must be selected according to the pneumatic circuit diagram, but the requirement that \"the solenoid valve must be properly energized while the interlock is powered off\" must be met.
Reply #42015-10-29
The so-called fail-safe requirement dictates \"zero voltage\" and zero current or low current, as well as disconnection, de-excitation, and spring return, for both the field side (inputs and outputs); The location of valve failures is determined by the properties of the process medium.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.