2015-11-27View Original

Thread Content

This post was last edited by *nht1 on 2015-11-27 13:11. What should be done in the event of a sudden power outage, with the steam valve still open, resulting in losses? How can it be optimized from a process design perspective?
Reply #22015-11-27
What is this process or procedure? No, add an air supply valve to the steam.
Reply #32015-11-27
It’s a steam electric control valve that is interlocked with a temperature sensor; when power is lost, the steam valve remains open and continues to heat, causing the pipes to soften. Is there any good method?
Reply #42015-11-27
Optimize it from the instrumentation side; just replace the steam valve or set it to turn off in case of a fault
Reply #52015-11-29
It must have been a sudden power outage. Edit it yourself and everyone will understand. . . . . .
Reply #62015-11-30
Adding a temperature-sensing series control should do it.
Reply #72015-12-01
Sir, what does temperature-based series control mean?
Reply #82015-12-03
For simple cases, just replace the control valve that is in the closed state; for more complex situations, install a UPS
Reply #92015-12-03
Temperature interlocking, FC valves, etc
Reply #102015-12-03
A pneumatic valve that closes when the air is released. Power loss – the solenoid valve releases air, and the valve closes.
Reply #112015-12-04
The motorized pump will stop operating when the power is cut off. You should set up a interlock between the signals of the important pumps and the air inlet valves; the air inlet valves should open when air is supplied, and they will close automatically when the power is lost.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.