HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Cable cross-sectional area calculation

2016-06-11View Original

Thread Content

A 220VAC UPS is used to supply power to downstream devices, which have a capacity of 2KVA each. The distance between these devices is 480 meters. What should be the cross-sectional area of the 3-core ZR-YJV cable used? What is the basis for the design?
Reply #22016-06-12
Based on the current-carrying capacity, the voltage drop caused by the cable length is taken into account (in other words, as the cable length increases, its resistance rises, resulting in a voltage drop). 2KVA / 220V = 9 A. According to the rule for cable current capacity, for cross-sections of 10 mm2 or less, 5 A is considered per mm2. Taking into account a distance of 480 meters, a cable with a cross-sectional area of 4 mm2 should be sufficient. That is, 3*4mm2 ZR-YJV cable (or 3*4mm2+1*2.5mm2 ZR-YJV cable). Please give me some advice.
Reply #32016-06-12
My god! The cable I designed is ZR-YJV 3x16mm2; the difference is huge. Voltage drop for a 6-square cable: △u% = 2△Ua%IL = 2*1.476*10*480/1000 = 14%; voltage drop for a 10-square cable: 8%; voltage drop for a 16-square cable: 5.5%. The value may be higher depending on the sensitivity settings chosen.
Reply #42016-06-13
Expert, I’ve learned it; I didn’t pay much attention to the voltage drop calculation.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.