The control valve amplifier makes exhaust noises frequently; I need the teacher’s help!

2015-12-07View Original

Thread Content

In the pneumatic accessories of the control valve, the booster relay experiences frequent automatic exhaust when not in adjustment mode, yet the valve position remains stable; the pressure gauge on the control valve fluctuates between 0.3 and 0.4, while the pressure from the instrument air supply remains stable. What’s going on? What should I do?
Reply #22015-12-07
So what should be done? Is it necessary to disassemble it for inspection? This valve is very important; I can’t risk using it with wires connected across it
Reply #32015-12-07
Spray soapy water on all the connections to see where there are leaks. If there is indeed a leak, try tightening it manually, but not too hard; if that doesn’t work, you’ll have to wait until the vehicle is stopped to deal with it.
Reply #42015-12-07
The main issue is that this sound isn’t continuous; it’s present sometimes and absent at other times, and sometimes it comes in bursts
Reply #52015-12-07
Generally, it’s air leakage. If you’ve checked and there are no issues, see if the connection fittings are loose. If that’s fine, then check whether there are any problems with the settings of the actuator. If not, and if the valve isn’t that important, set a higher dead zone value and observe again (you can also try using a different actuator). If that still doesn’t work, check by performing the operation to see if air is leaking from that exhaust port (the diaphragm may be damaged).

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.