Issues with MODBUS RTU communication between Siemens S7-400H and Honeywell PKS3000?

2015-12-12View Original

Thread Content

The Honeywell PKS3000 (DCS) reads data from the Siemens S7-400H (PLC) via MODBUS RTU. The MODBUS addresses provided by PLCs all start with 4, such as 40001, etc., without any distinction between DI\DO\AI\AO. However, when reading with DCS, the register type must be selected. The problem is that by following the addresses provided by the PLC, it is not possible to read all the data; only certain types (appears to be DI) can be read. For AI, in order to read its data, the address must be changed to start with 3, such as 30001, etc. I was wondering, is it normal for this to happen? What is the reason? Is there a problem with the settings in DCS or PLC?
Reply #22016-01-26
Check the MODBUS communication configuration for 400; it seems that only direct communication is possible, with DB, M, and Q as the areas involved
Reply #32016-01-26
The PKS serves as the master station, while the S7-400s act as slave stations; the addresses assigned to the S7-400s all start with 4, so there is no issue at all. Modbus addresses starting with 4 represent the Holding Registers, in other words, the area for readable and writable analog values. Addresses starting with 3 refer to the Input Registers area, or the read-only analog values area. The register area starting with 4 can fully fulfill the functions of the register area starting with 3.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.