First, describe the fault symptoms: The factory has an ABB variable frequency drive motor, with the drive unit being the ABB ACS1000. This fault has occurred twice; in one instance, the speed dropped unexpectedly, with the rotation speed falling from 160 RPM to 140 RPM. After the operator noticed this, they increased the speed on-site using a variable resistor, and the motor resumed normal operation. The other time was when it dropped from 204 rpm to 0 (the current overload interlock stopped the machine during this speed reduction); the interval between the two incidents was about 2 months. The speed control circuit consists of a variable resistor, a resistance transmitter, an inverter, and a DCS; the DCS merely displays the speed. After the speed reduction fault occurred, no fault code was detected in the frequency converter; ABB technicians also found no error messages. However, during maintenance, it was found that the capacitors on some circuit boards were bulging. I would like to ask fellow sailors if you have encountered similar problems? Please help analyze the cause of the failure. Thank you.
What does it mean when the current overload triggers a chain stop during the speed reduction process?
Is a low rotation speed caused by a high load or a low power supply voltage?
Low speed, high torque, low voltage, high current; normal overload trip
The inverter has a voltage-to-frequency ratio curve; check the instructions to see if there is an issue with the settings
Yes, interlocking stop is no problem. It was just a sudden slowdown; it’s not clear what caused it.
The frequency and voltage parameters of the inverter are consistent with those on the motor nameplate.