This post was last edited by hjztbwg on 2016-1-7 09:29. The height of a certain industrial building is 15 m; the total heat loss required for heating the building in winter, as calculated, is 1500 kW. The heat transfer coefficient of the exterior windows is 3.5 W/(㎡·K). What should be the heat loss due to cold air infiltration? Answer: B (A) 375kw (B) 450kw (C) 525kw (D) 600kw
Reply #22015-12-30
A certain industrial building is 15 m in height. The calculated total heat loss of the building’s envelope during winter heating is 1500 kW. The heat transfer coefficient of the exterior windows is 3.5 W/(㎡·K). What should be the heat loss due to cold air infiltration? A (A)375kw (B)450kw (C)525kw (D)600kw
Reply #32015-12-30
A certain industrial building is 15 m in height. The calculated total heat loss of the building’s envelope during winter heating is 1500 kW. The heat transfer coefficient of the exterior windows is 3.5 W/(㎡·K). What should be the heat loss due to cold air infiltration? (B)450kw
Reply #42015-12-30
A certain industrial building is 15 m in height. The calculated total heat loss of the building’s envelope during winter heating is 1500 kW. The heat transfer coefficient of the exterior windows is 3.5 W/(㎡·K). What should be the heat loss due to cold air infiltration? (B) (A)375kw (B)450kw (C)525kw (D)600kw
Reply #52015-12-30
Answer: B. Analysis: According to D.0.4 of the Thermal Code, the heat loss due to cold air entering indoor spaces through gaps in doors and windows in industrial buildings can be estimated using Table D.0.4. The heat transfer coefficient of the exterior window is 3.5 W/(m2·K). According to clause 2.2.6 of the \"Technical Measures,\" this is a double-glazed window; therefore, cold air infiltration accounts for 30% of the total heat loss, resulting in a cold air infiltration amount of 1500*0.3=450 Kw
Reply #62015-12-30
B, double-glazed window 1500*0.3=450KW

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.