KVVRP control cable, issue regarding the distance to the hardwired DCS.

2016-01-03View Original

Thread Content

I have a question: the cable used is KVVRP 10*1.0. It is a 1-5V voltage signal. The distance from the DCS is 400 meters; will it affect the signal? The control cables and power cables run in the same tray, separated from each other by a partition in the middle.
Reply #22016-01-03
The shielded one should work, right?
Reply #32016-01-03
Voltage signals are not suitable for long-distance transmission; 400 meters is too far, while a few dozen meters is acceptable.
Reply #42016-01-03
With partitions and shielding layers in place, control cables and power cables can be run on the same tray, but this is not recommended.
Reply #52016-01-03
Given such a long distance and the fact that it is a voltage signal, it is recommended to convert it to a current signal for transmission.
Reply #62016-01-04
The distance is too long, which will cause a voltage drop
Reply #72016-01-04
1_ A 5V voltage signal will experience voltage drop when transmitted over a distance of 400 meters. It is recommended to add a signal isolator to convert it into a 4-20mA current signal for transmission
Reply #82016-01-04
What type of signal is the 1-5V voltage signal from the poster? If it is a communication signal, KVV cannot be used. @jiaguoyun
Reply #92016-01-05
Original poster, first of all, as the user mentioned above, the distance is too great, which results in excessive voltage signal loss. Secondly, even if your signal is a standard current signal, the cross-sectional area of the cable you chose is too small due to the large distance; for 400V, I think at least 1.5mm2 would be necessary.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.