2016-01-24View Original

Thread Content

Is your unit equipped with a CO incinerator? My unit does not feature full regeneration; it has an incinerator. What is the fuel used for the CO incinerator? Here, the fuel comes from the company’s high-pressure gas pipeline network. In recent days, Shandong province has experienced the lowest temperatures in 30 years, with temperatures dropping to minus 18 degrees. My unit’s high-pressure gas pipeline network lacks heat tracing, which has led to freezing issues. I would like to discuss the following questions: 1. Does the unit operate in full regeneration mode or incomplete regeneration mode? Is there a CO incinerator installed? 2. What is the fuel used for the CO incinerator? 3. Does the high-pressure gas pipeline have heat tracing?
Reply #22016-01-24
1. Here, we use complete regeneration (that is, single-stage regeneration); there is no CO combustion furnace installed (I have seen systems with two-stage regeneration). 2. The fuel for the CO combustion furnace is high-pressure gas. 3. In our case, insulation and hot water heating are used for the high-pressure gas. Your process should be as follows: first, conventional regeneration is used to remove CO, but an external heat exchanger is still installed; second, complete regeneration is employed. The primary flue gas and the secondary flue gas are treated separately; after the primary flue gas has done work through a flue gas turbine, it merges with the secondary high-temperature oxygen-containing flue gas to enter the CO combustion furnace, where CO is completely burned using less supplementary fuel
Reply #32016-01-24
We are fully regenerative, with no CO burners. Neither the high-wattage nor the low-wattage units have heating, and as a result, the high-wattage unit froze yesterday! It turned out that the dry gas line inside the unit didn’t have heating, so it would freeze frequently in winter; heating was added during the renovation, and now it’s much hassle-free! Based on the actual situation, it must be added. Otherwise, normal production will be affected, and our brothers will suffer from the cold!
Reply #42016-01-24
1. We have a small device that features two-stage regeneration. There is a C0 combustion furnace. 2. The fuel for the C0 combustion furnace is high-pressure gas. 3. The high-pressure gas line does not have heat tracing, but it is equipped with a gas liquid separator tank; condensate is drained regularly on a shift basis, and freezing blockages have never occurred. Of course, this is related to the ambient temperature; here in winter it never drops below -5°C.
Reply #52016-01-25
Here, we’ve had no problems even at minus 10 degrees; this year, it froze at minus 18 degrees. It’s necessary to install heating elements during maintenance
Reply #62016-01-25
This is complete regeneration; incomplete regeneration means burning the flue gas again in a combustion furnace, right? Solve. The overheating furnace we use here is equipped with high-wattage units; however, these units don’t have any heating system, so they froze a few days ago at minus 15 degrees. We then added insulation, and we also drain the liquid once per shift
Reply #72016-01-25
High-pressure gas contains some condensed oil and moisture, and freezing can occur when problems arise; it is best to install heating lines, as pipes with such heating lines avoid freezing issues altogether.
Reply #82016-01-25
Last night the temperature dropped to minus 8 degrees. This morning, when I turned on the steam and water valves at the service station, there was nothing – everything was frozen solid. Minus 8 degrees is basically a new record low. :lol
Reply #92016-01-27
Fuel gas systems in the north are equipped with heat tracing and vaporizers; in case there isn’t enough gas, liquefied gas must be added as a fuel source, which is why heat tracing is very important
Reply #102016-01-31
Complete regeneration does not require a furnace; insulation is preferred
Reply #112016-01-31
The dry gas line should be insulated; the fuel is carbon monoxide and gas, and complete regeneration does not require a furnace

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.